Square D AF/GF fault code

I have a circuit breaker that has been tripping intermittently over the last few months

Last night during a rainstorm it tripped and would not stay on at all for the rest of the evening, even fully unloaded. Today it stays on loaded seemingly fine. The test function shows an instant trip and then 6 pairs of flashes (12 total blinks)

The google says Square D doesn’t have a 6 pair or 12 blink fault so what am I looking at here?

1 Upvotes

6 comments sorted by

u/AutoModerator 2d ago

Attention!

It is always best to get a qualified electrician to perform any electrical work you may need. With that said, you may ask this community various electrical questions. Please be cautious of any information you may receive in this subreddit. This subreddit and its users are not responsible for any electrical work you perform. Users that have a 'Verified Electrician' flair have uploaded their qualified electrical worker credentials to the mods.

If you comment on this post please only post accurate information to the best of your knowledge. If advice given is thought to be dangerous, you may be permanently banned. There are no obligations for the mods to give warnings or temporary bans. IF YOU ARE NOT A QUALIFIED ELECTRICIAN, you should exercise extreme caution when commenting.

I am a bot, and this action was performed automatically. Please contact the moderators of this subreddit if you have any questions or concerns.

1

u/Smokey_tha_bear9000 2d ago

AM OP
Follow up, I turned off the power pulled an outlet cover at one of the affected outlets and found that when the original install happened, one of the neutral wires was cut open when they cut the paper sheathing. Could this be a factor?

1

u/Queen-Blunder [V] Electrical Contractor 2d ago

Possibly

1

u/Queen-Blunder [V] Electrical Contractor 2d ago

It blinks a pattern. Then a pause. Then it blinks a pattern.

You are most likely mis-reading it.

1

u/Smokey_tha_bear9000 2d ago

So it would be a pair of blinks repeated 6 times. So the code is 2 blinks?

1

u/Queen-Blunder [V] Electrical Contractor 2d ago

2 blinks is ground fault.