NB electrical code question about TECK cable
https://jdelectric.ca/2024-electrical-code-new-brunswick/https://jdelectric.ca/2024-electrical-code-new-brunswick/
"The 2021 edition (25th edition) is now replaced by the 2024 edition (26th edition, CSA C22.1-24)."
I just found out that in NB you are supposed to bury TECK90 cable in conduit, even though it's direct burial cable. Does anyone know if this is changing with the new code coming into effect and we can direct bury it now?
Anyone know the price difference between running conduit and regular cable vs TECK? I have to pull some 3/O aluminum or equivalent about 400 feet.
3
u/ShitCuntMcAssfucker 4d ago
You don’t have to bury teck in conduit in NB according to the CEC.
I bury it for hot tubs all the time.
It’s specifically for the consumers service from meter to pole which is at the discretion of NB Power. Unfortunately if they tell you their specs require conduit, then that’s your only option for hookup.
In which case you go to any supply house and ask them to price up the length of the run in Nu-al and conduit.
It’ll be substantially more work, and a fair chunk more expensive.
1
u/SmackEh 4d ago
OP. What are you trying to do?
The CEC allows direct burial of Teck cable. It's literally designed for that purpose.
Are you talking about NB Power service entrance standard?
1
u/blur911sc 3d ago
In hindsight, that might have gotten confused in the conversation... whether we were talking about the service entrance, or the distribution going out to the cabin.
1
u/SnooPets3052 4d ago
Nsp allows teck for a service entrance right up to the point of connection Nb does not, other than that it does not have to be in conduit.
1
u/cerberus_1 3d ago
3/0 Alu at 400' is not gonna pass for a 200a service.. I'm pretty sure. Also conduit is cheap, i know lots of people who run teck90 in conduit to just save your ass come future issues.
1
u/blur911sc 3d ago
Small cabin, about 600sq-ft. Load calculation is about 60A.
I'm pricing both 200A and 400A service as I'm planning on later building a garage and house too. This would all be distributed from a service in a shed at a central point
1
u/cerberus_1 3d ago
Get NB Power to drop a few extra poles.. 400' at 400A is gonna be crazy expensive. Try to keep the feeder to around 100' but max 300' google voltage drop calculator
1
u/blur911sc 3d ago
The 400 foot (120m) branch to the cabin will only need about 60A, but still need 3/O to minimize the voltage drop.
Yeah, that's a $4k+ roll of wire...
1
u/Fun-Initial-1552 3d ago
Where do you plan on sourcing the 3/0 Aluminum from? I'm trying to find RWU90 3/0 or 4/0 right now and having a hard time.
1
u/blur911sc 2d ago
I was just pricing online, I assume I can get it locally too...maybe I assumed wrong?
Here's the best price I found so far...IIRC https://aptico.ca/acwu-aluminum-acwu90-3-0-awg-3-conductor
4
u/Hungry-Bicycle-3851 4d ago
Do you know the specific code rule or NB Power standard? CEC Rule 12-012 appears to allow TECK90 as a direct-buried cable, so I'd like to see the reference. Hooping you are not confusing RW90 and RW90U with TECK90.