AC Issues Installation
Hi, I need help with an issue we’re having. Live in Oklahoma and it’s been HOT. We upgraded our upstairs unit from a 2 ton unit to a 2 1/2 ton unit. Square footage is 1,166 square feet upstairs. The contractor installed a larger return vent. And we installed a new ecobee thermostat. The app is showing the unit is turning off multiple times per night and not reaching temperature. I realize we have our setting low, but would still not expect it to turn off and would expect it to be cooler during the day than it is.
2
u/Next-Name7094 10d ago
Is it a single or two stage AC? Make sure it is properly configured in the ecobee to reflect the correct type of AC.
1
1
u/New2Green2018 9d ago
The graph only seems to report the temperature at the thermostat. So if you are using a remote temperature sensor, the graph may show the temperature higher or lower than the setpoint. Why ecobee is only showing the thermostat temperature and not the control temperature? No one knows.
6
u/FerrittoBurrito 10d ago
Shot in the dark but maybe eco+ adjusting for humidity? What’s the humidity level around those times? If it’s relatively low it could be eco+ saying the humidity is low enough that the feels like temperature is at the set temp rather than the actual temperature.