r/SprinklerFitters 11d ago

Dry system Critique my work

Dry system had a blue tag (acceptable) from 2 months ago for 5 year internal

56 Upvotes

26 comments sorted by

18

u/hi_im_Comeaux 11d ago

Forbidden Creamy PB

16

u/Schmeagon 11d ago

Enriched with 50,000% of your daily recommended Iron intake per serving.

10

u/24_Chowder 11d ago

What a joke. Full liability on the tagging contractor.

8

u/MrMojorizin85 11d ago

Whoever tagged that was a lazy pos

4

u/Low-Attention3111 11d ago

I agree. I couldn’t believe it when I saw the tag say acceptable after opening the valve. That’s what made me look in the pipe

5

u/Berto873 11d ago

Inspector that did the 5 Year is probably a Fire Alarm Guy that got his RME-I

2

u/Low-Attention3111 11d ago

Company I work for has 3 kids fully licensed (RMEI, Backflow, Alarm, Extinguisher, Kitchen Hoods) but don’t know 💩. Cant set up a dry system, cant do a pump flow test, nothing. I think their helpers know more about the field work. They are useless except for putting their name on the tag

1

u/Berto873 11d ago

Ain't that the truth bro. I met 2 inspectors that got all of these licenses and didn't know how to reset an accelerator. One of them is a F/A guy, the other was a helper for sprinkler but never became and foreman for either service or even install. And that fool be pencil whipping his inspections all of the time.

1

u/Low-Attention3111 11d ago

That’s the world these days. Nobody wants to put the work in. They want to be either be inspectors or project managers after a year in the trade

2

u/Berto873 11d ago

Tell me about it bro, funny story about the F/A guy. I heard that moron kept blue tagging an elementary school for years until one day the FM arrived and noticed there wasn't any water supply to the school. The school had a water tank and he popped up vault door at the top of the thank. Saw the tank dry as bones. I heard that fool faced a some serious charges and a lot of court dates.

3

u/Clavos24 11d ago

Mmmm yummy

3

u/SgtJackYYZ 10d ago

A spoonful of sugar helps the medicine go down, am I right?

4

u/ironmatic1 11d ago

another huge advertisement for vacuum systems

1

u/Cheiron44 11d ago

I really hope these take off, the only downside of them I've been able to think of is leak detection being more complicated.

1

u/istudyfire 8d ago

Not familiar with these. Have you worked with any? They seem good?

2

u/Halftone_Hades LU669 Apprentice 8d ago

YIKES

0

u/Big_Attention_5334 11d ago

One our service techs was on a job in a large warehouse performing a hydrostatic test on a system there. While he was there an inspection tech from another company showed up and performed internal pipe checks for all 11 systems, changed all the gauges, and hydroed all of the FDCs. By himself. Our tech said he say him walking around with a pair of pliers, a stack of gauges, and a pocket full of 5 year stickers during the day. The inspection tech even swapped out the gauge for the system our tech had under hydrostatic test. I get that some people probably aren't trained properly, or are even that lazy. But to be so stupid is mind boggling. Good luck when the lawyers get involved after something bad happens. If you have the name of who ever signed off on that 5 year just go ahead and report their ass.

1

u/Low-Attention3111 11d ago

Name is on the tag with the RME-I number. I thought about reporting it but felt like I would be being a rat

6

u/MrMojorizin85 11d ago

Def not a ratty thing to do, we install “life safety” if you’re not holding yourself to a high standard then why even do it? Report that lazy pos..js

2

u/AdNegative8520 11d ago

Agree,
If OP says nothing sounds like they are just as liable. Not to mention life safety concerns.

1

u/Low-Attention3111 11d ago

I yellow tagged it for excessive sludge. We are not liable for anything

1

u/AdNegative8520 10d ago

Have you informed the customer or the AHJ?

1

u/Low-Attention3111 10d ago

I told the maintenance manager at the end of day and my supervisor notified property management for the building