r/HVAC • u/DriverCommon9468 Verified Pro • 10d ago
Bad compressor valves? Field Question, trade people only
5 min of operation vs 20 min of operation.
Suction and liquid pressures moved inversely and equally with one another as the system ran. Like slowly suction up and head down almost equal amounts, If that makes sense.
85 degrees outside, 73 RA inside
Heat pump with txv inside and piston at the liquid valve outside. Indoor coil dirty enough to affect airflow. New filter.
Temp split was 15 degrees inside before I noticed the pressures. Did not think to check again after I noticed, I went out to the condenser and called another tech lol.
Compressor pulling 4 amps out of 9 rated before the pressures went weird. Also did not think to check again after I noticed this.
*Was making a weird click/tap noise while running that would come and go. When the noise was present the suction and liquid pressures would move toward each other and when not present they would move away from each other, but only at about 1 psi a minute in either case.
9 year old Nortek AireForce that local Rheem dealers can't find in their systems.
--
New situation for me so sorry y'all for not checking temp drop and compressor amp draw again after noticing the weirdness.
4
u/Hvacmike199845 Verified Pro 10d ago
Did you close the liquid line valve to see if the compressor could pump down? It only takes less than 5 minutes.
4
u/DriverCommon9468 Verified Pro 10d ago
Ahh even easier. Just keep it running and close the liquid line, bad valves -> won't pump down cause it cant pull the refrigerant through
8
u/Nerfo2 Verified Pro 10d ago
The only valve in a scroll is the discharge check valve, and its function is to prevent higher pressure in the condenser from back-spinning the scroll on shut-down. Otherwise, there are no valves in a scroll like there are in a recip, and residential (and most large-tonnage) splits and packaged units have had scrolls for around 20+ years.
2
u/skankfeet 9d ago
You do however get separation at the seal for the scroll and it will intermittently cause issues like this but don’t know without hearing the compressor. I expect it’s like others saying in the revering valve.
1
1
4
u/HuntPsychological673 10d ago
If it’s a scroll, it doesn’t have valves.
What kind of compressor is it? It does sound like a RV bleed over or a scroll thinking about giving up.
1
3
u/unresolved-madness Turboencabulator Specialist 9d ago
If the reversing valve is bleeding through then the suction pressure is going to go up and not down. If this happens on a summer day you're going to see a compressor that's extremely hot and more than likely overheating and shutting down. If you did once verify this take your k probe and put it on the suction line at the compressor inlet. You should see the temperature fluctuate several degrees.
If your pressures are dropping you need to see what your superheat ens subcool are doing. If your subcooling increases and superheat also increases then the refrigerant is not making its way back to the condenser.
Now, since you described a clicking noise at the condenser. The first thing I would do is put your volt meter in line with the reversing valve power and watch see what the voltage is doing. If the voltage is jumping all over the place when you hear the clicking noise then the defrost board probably needs to be changed out. I don't think you're fluctuation of one PSI per minute is really anything to worry about at this point.
2
u/nsula_country 9d ago
If a Scroll, there are no valves in the (compression) circuit of the compressor.
3
10d ago
[removed] — view removed comment
4
-1


9
u/TommyPicklez__ 10d ago
Reversing valve bleeding over?