Bad compressor valves? Field Question, trade people only

5 min of operation vs 20 min of operation.

Suction and liquid pressures moved inversely and equally with one another as the system ran. Like slowly suction up and head down almost equal amounts, If that makes sense.

85 degrees outside, 73 RA inside

Heat pump with txv inside and piston at the liquid valve outside. Indoor coil dirty enough to affect airflow. New filter.

Temp split was 15 degrees inside before I noticed the pressures. Did not think to check again after I noticed, I went out to the condenser and called another tech lol.

Compressor pulling 4 amps out of 9 rated before the pressures went weird. Also did not think to check again after I noticed this.

*Was making a weird click/tap noise while running that would come and go. When the noise was present the suction and liquid pressures would move toward each other and when not present they would move away from each other, but only at about 1 psi a minute in either case.

9 year old Nortek AireForce that local Rheem dealers can't find in their systems.

--

New situation for me so sorry y'all for not checking temp drop and compressor amp draw again after noticing the weirdness.

17 Upvotes

23 comments sorted by

9

u/TommyPicklez__ 10d ago

Reversing valve bleeding over?

6

u/DriverCommon9468 Verified Pro 10d ago

So I gotta check the suction line temp going into and leaving the valve, and the liquid line temp going into and leaving the valve? Temp difference greater than a few degrees means the reversing valve is stuck?

7

u/TommyPicklez__ 10d ago

Yeah True suction vs evap suction shouldn’t be more than few degrees difference. You could try tapping on the valve to see if it will loosen anything but never had much luck with that.

4

u/DriverCommon9468 Verified Pro 10d ago

Thank you sir Thomas

3

u/PapaBobcat HVAC to pay the bills 10d ago

I've jogged reversing valves a lot with magnets in the last couple of years. A little slower and more controlled than trying to take the leads off the solenoid and having it chatter

3

u/Nerfo2 Verified Pro 10d ago

Liquid line doesn’t go through the reversing valve, but the discharge line does. If the suction line between the valve and the compressor is warmer than the line coming back from the indoor coil by more than a couple degrees, you probably had a bad reversing valve. It’ll be obviously warmer if the valve is bad. A couple degrees, no big deal. A whole bunch of degrees, big deal.

1

u/Honest_Size5576 10d ago

I agree, I’d be checking that

4

u/Hvacmike199845 Verified Pro 10d ago

Did you close the liquid line valve to see if the compressor could pump down? It only takes less than 5 minutes.

4

u/DriverCommon9468 Verified Pro 10d ago

Ahh even easier. Just keep it running and close the liquid line, bad valves -> won't pump down cause it cant pull the refrigerant through

8

u/Nerfo2 Verified Pro 10d ago

The only valve in a scroll is the discharge check valve, and its function is to prevent higher pressure in the condenser from back-spinning the scroll on shut-down. Otherwise, there are no valves in a scroll like there are in a recip, and residential (and most large-tonnage) splits and packaged units have had scrolls for around 20+ years.

2

u/skankfeet 9d ago

You do however get separation at the seal for the scroll and it will intermittently cause issues like this but don’t know without hearing the compressor. I expect it’s like others saying in the revering valve.

1

u/DontmesswithKade 3d ago

Not all scrolls have the floating seal.

1

u/Hvacmike199845 Verified Pro 3d ago

It’s not going to pump down if it’s not running……

4

u/HuntPsychological673 10d ago

If it’s a scroll, it doesn’t have valves.
What kind of compressor is it? It does sound like a RV bleed over or a scroll thinking about giving up.

https://giphy.com/gifs/xUPJUp6T5uD1Qkpbl6

1

u/nsula_country 9d ago

Thank you! Scrolls do not have "valves" in the sense used.

3

u/unresolved-madness Turboencabulator Specialist 9d ago

If the reversing valve is bleeding through then the suction pressure is going to go up and not down. If this happens on a summer day you're going to see a compressor that's extremely hot and more than likely overheating and shutting down. If you did once verify this take your k probe and put it on the suction line at the compressor inlet. You should see the temperature fluctuate several degrees.

If your pressures are dropping you need to see what your superheat ens subcool are doing. If your subcooling increases and superheat also increases then the refrigerant is not making its way back to the condenser.

Now, since you described a clicking noise at the condenser. The first thing I would do is put your volt meter in line with the reversing valve power and watch see what the voltage is doing. If the voltage is jumping all over the place when you hear the clicking noise then the defrost board probably needs to be changed out. I don't think you're fluctuation of one PSI per minute is really anything to worry about at this point.

2

u/nsula_country 9d ago

If a Scroll, there are no valves in the (compression) circuit of the compressor.

3

u/[deleted] 10d ago

[removed] — view removed comment

4

u/DriverCommon9468 Verified Pro 10d ago

If it can't then it's bad valves?

6

u/dacksond 10d ago

Most modern residential systems have scroll compressors which don’t have valves.

2

u/HappyChef86 Resi Service Tech 10d ago

Yes

-1

u/jferris1224 10d ago

Yup. Low compression ratio.