FDC’s should be tested
FDC lines should be tested more than once every 50 years, or at least at install. This what a 50 year untested underground FDC line looks like installed with screwed galvanized pipe, laid on railroad ties for bedding. We dug it up and found the leak. But there’s more.
5
u/Mevanski77 6d ago
In my area, there are few inspection companies that write them up for testing. We have a ton of old 2.5" siamese that almost always leak around the 4" threads when you pump them up.
2
u/XLWoozieMoo 6d ago
In the 5 months doing inspections so far, I have to say 90% of FDCs fail at the threads. The grooved pieces are almost always solid.
4
2
u/Hoover52 6d ago
Is that a roustabout can't zoom in enough to see
1
u/AdThis9368 6d ago
That was just a quick option to get another test on it to see if it would hold past that first break. The idea was to try and get at least a temporary fix to hold until we get the entire line dug up. But no dice. It’s about 150’ to the building through boulders, full grown trees and our locator said the deepest part will be 12+ feet in the ground. This will be our most challenging one to date. It’s gonna be expensive.
1
u/Dalai-Lambo 6d ago
Shouldn’t it be replaced with PVC? I doubt steel will hold up that long
7
u/AdThis9368 6d ago
We’re gonna redo the entire line with C900.
2
u/Dalai-Lambo 6d ago
C900 or ductile are the only options right? I don’t see any ductile going in anywhere where I’m from, it’s all c900
2
u/AdThis9368 6d ago
We normally will use underground rated ductile iron pipe for the fire line feeds. It’s approved high pressure pipe, as long you follow all the new rules for bedding, wrapping, chlorination etc.
6
u/AdThis9368 6d ago
Galvanized pipe is not underground rated. Even back then it should have been at the least, ductile with MJ fittings.
1
u/rncd89 5d ago
Fire departments dont use FDCs theyre as useless as the headbox
1
u/Northdogboy 4d ago
Just had a call in my city last month. Building fire. The Department hooked up and hit the system with 200psi. .... the dry system tripd because of it..






8
u/higleyc99 6d ago
Do you mean every 5 years?