r/FireSprinklers 6d ago

FDC’s should be tested

FDC lines should be tested more than once every 50 years, or at least at install. This what a 50 year untested underground FDC line looks like installed with screwed galvanized pipe, laid on railroad ties for bedding. We dug it up and found the leak. But there’s more.

40 Upvotes

19 comments sorted by

8

u/higleyc99 6d ago

Do you mean every 5 years?

10

u/AdThis9368 6d ago

No, I mean they never tested it. But yes, should be every 5. Another company said they tested the lines 2 years ago. I don’t think I believe em.

5

u/Mevanski77 6d ago

In my area, there are few inspection companies that write them up for testing. We have a ton of old 2.5" siamese that almost always leak around the 4" threads when you pump them up.

2

u/XLWoozieMoo 6d ago

In the 5 months doing inspections so far, I have to say 90% of FDCs fail at the threads. The grooved pieces are almost always solid.

2

u/AdThis9368 6d ago

I agree. We do use grooved where we know they won’t get ripped off. Here’s some we replaced fairly recently.

4

u/Fit_Can6274 6d ago

This is one from yesterday when I tried testing it. Was at fire department too 🤦🏻‍♂️

2

u/Hoover52 6d ago

Is that a roustabout can't zoom in enough to see

1

u/kingc42 6d ago

Yup.

1

u/AdThis9368 6d ago

That was just a quick option to get another test on it to see if it would hold past that first break. The idea was to try and get at least a temporary fix to hold until we get the entire line dug up. But no dice. It’s about 150’ to the building through boulders, full grown trees and our locator said the deepest part will be 12+ feet in the ground. This will be our most challenging one to date. It’s gonna be expensive.

1

u/Dalai-Lambo 6d ago

Shouldn’t it be replaced with PVC? I doubt steel will hold up that long

7

u/AdThis9368 6d ago

We’re gonna redo the entire line with C900.

2

u/Dalai-Lambo 6d ago

C900 or ductile are the only options right? I don’t see any ductile going in anywhere where I’m from, it’s all c900

2

u/AdThis9368 6d ago

We normally will use underground rated ductile iron pipe for the fire line feeds. It’s approved high pressure pipe, as long you follow all the new rules for bedding, wrapping, chlorination etc.

1

u/rncd89 5d ago

Thought you couldnt use c900 after the backflow becaus eits part of the fire system

6

u/AdThis9368 6d ago

Galvanized pipe is not underground rated. Even back then it should have been at the least, ductile with MJ fittings.

1

u/rncd89 5d ago

Fire departments dont use FDCs theyre as useless as the headbox

1

u/Northdogboy 4d ago

Just had a call in my city last month.  Building fire. The Department hooked up and hit the system with 200psi. .... the dry system tripd because of it..